Plumbing help

thataway

Active member
I have a problem which has me a bit puzzled, and although it is not directly C Dory related, I hope that some of the members have some good ideas as to what is causing the problem.

Several days ago I noted a warm area of the utility room floor. Yesterday evening: no hot water or water pressure. We shut off the hot water and this AM "American Leak Detectors" pinpointed the leak ($285 right where it was hot several days ago).

The plumber was here for about 4 hours, and the 3/4 inch soft copper hot water pipe buried 6" under the 5" re-inforced slab is completely shot. It looks like bark peeling off a tree. The house is only 8 years old. The cold water pipe is fine. We are going to have to replumb the entire hot water system--through the atic. This is a 3600 sq foot 4 bath house, with some ceilings as high as 16 feet, so not an easy job. But that is life.

The plumber thinks it was a lightning strike. I think perhaps some form of electrolysis. Any thoughts:


copper_pipe_002.jpg
 
Bob, any time a C-Brat starts with the word "Help", or "Advice" we know we've got a live one.

Lightning destroys by high current, and the resultant IR heat melts things. As far as I can see, nothing is melted, and the other choice is corrosion. Is there any voltage between the hot water heater and ground? That would explain electrical corrosion. Higher water temp could cause chemical corrosion and actually that's what it looks like. At least from California.

Check with your neighbors, and see if they've been corroded also.

Good luck, boris
 
Bob,
Sorry, It does look like a mess. It seem to me you are assuming, all the hot water pipes thru out the house are in a simular condition as the section that deteriorated. I hope your assumption is incorrect.
I had a simular condition in a 1/2 bath in the lower floor of my home. It is also the closes to the hot warer tank. The problem was isolated to the hot water pipe under the cabinet, easy fix.
The hot water line under your slab turns up to access your first sink, faust. etc. I would locate that or an easy line, coming out of the slab and cut a section to determine if the corrosion is continuous, or isolated. If it only effects the pipes under the slab , I would run the new lines outside the foundation, You can get by with that in Florida, not here in Idaho or Alaska, Intercept the 3/4 hot water line a convevent place to feed the system. I hope it will be that simple.

Gary
 
Lightning does strange things down here.I agree that usually it melts and fuses. It can cause perforations in pipes--and fuse sand, plus travel through the wet ground and water. Our thoughts is that lightning in wet soil may act differently than in dry and hotter environments. But ou bring up good points!

This almost looks like the prop on the Cal 46 after a strike took out the diode on the alternator and the new owner was allowing 130 amps of 12 volt DC to go to "ground". The only direct electrical connection with these pipes is a bathroom Jacuzi tub. Good suggestion to check the current and voltage potentials. I'll do this in the AM. We have several ground rods--on the Genset, the main pannel, the pool/jacuzzi and the dock. All of these are in good shape. No direct ground to the water pipe, except it is in earth.

We did loose the power supply in a computer when I was gone to Calif in Dec (melted capaciters and resisters--no other problems, and it was on a good surge protector).

Gary, the under the slab piping is soft copper tubing. We thought it went directly to the kitchen sink, but that was not to be. After cutting the wall, there is no manufold. We think that the 3/4" line goes to one of the bathrooms, and then is reduced to 1/2" and returned to the sink. Tomarrow we are going to high pressure (air) test these lines. The half inch look OK so far. But the sink is basically on an island, so we have to back feed from some other area. We may just abandon all of the line under the floor, except this one. It will be easier and better cosmetically to run new water lines in the attic than outside. We do have decent access (one walk in and one trap door) to the attic and can ID where the sink walls are. What is strange is that we thought that the 3/4" water line went to the sink, and then split to 1/2" to each bath. It now appears that the 3/4" line to one bath, and then splits back to the other bath and kitchen. When we are through we will put in a circulating hot water pump (on a timer). We had a circulating hot water system on the boat. This conserved water and made sure we always had hot water,

We also have the name of the plumber who did the original install, and my plumber will be calling him first thing in the morning.

Thanks and "keep them coming"!

Bob
 
Bob, three thoughts:

1. Where is the electrical ground for the house? Is it OK?

2. What is your water source? Well? Municipal water?

3. Have you replaced the hot water heater? I assume it is an electric model -- is it wired in properly? Does it have an element that has lost its insulation?

I agree some sort of electrolysis/misdirected current must be the cause.

For the copper to corrode like that, it would have to have become the default ground, perhaps carrying current for something else that has a short to ground, I think. What could have failed?

You got me puzzled, for sure!
 
Bob, I would also suggest you consider the possibility of substandard materials, e.g., impurities or manufacturing defects in the piping itself. Maybe the builder cut some corners? Maybe the supplier did? Maybe just bad pipe?

I will now return to lurking in discussions totally above my pay grade. :shock:

Warren
 
Bob,

We built our house in 2001 and they suggested and used plastic plumbing instead of copper, partly because of the problems they were seeing in the imported copper pipe. I'm now very glad they did. I'd suggest using it for the repairs.

Won't your homeowners insurance cover this? I sure hope so for your sake.

I have zero expertise in this area, so I won't hazard a guess as to the cause. Best of luck.
 
There are two possible sources of corrosion of copper piping I have seen. First, is the corrosion on the inside or outside of the pipe. If it is on the outside (doesn't look like this in the photo), it may be galvanic corrosion in the ground, and the pipe in the walls etc will be OK. It will be the pipe in contact with the ground that will need to be replaced. This shows up many times in utility energy audits when the customer complains of a high bill.

The second form of corrosion is internal to the pipe, and this can be galvanic due to dissimilar metal forms, ie: the pieces of pipe, joints, fittings and elbows may be dissimilar alloys. It can also be due to corrosive water flowing in the pipes. It can also be cavitation or grain boundary corrosion due to high water speed in the pipes. I have seen this in homes and restaurants that have a recirculating hot water pump to have instant hot water in the whole house. It usually shows up in elbows and fittings where the water changes direction, and usually on the outside of the turn. I recommend only running the pump when you are going to use hot water due to the high probability of cavitation or grain boundary corrosion due to the water speed in the pipes. This kind of damage will be on the inside of the pipes, and will be throughout the hot water piping of the house.

Good luck.
 
You could install small tankless instant hot water heaters at each bathroom, kitchen, laundry, etc., since your cold water pipes are good.
Roger
 
Is your hot water heater pipes grounded across the cold and hot lines? Is it electrolysis from the hot water heater? Is the anode worn? Just a bunch questions from a bystander.

Our Fl home was built in 50's and has solid heavy wall copper pipe and no problems to date and definitely not soft. If you replace with PET or something using no metal please post an update.
I expect someday we will face the same issue.
 
What about the anode in the hot water tank? I guess it's actually there to protect the tank rather than the piping but with these sort of problems I'd check it. I'm assuming you have and electric hot water heater. Also with mulitple grounds if they aren't all tied together I've seen problems with stray voltages between the grounds. Ideally all ground rods should be tied together but this isn't always practical or possible. Also I think where the line is connected to the water tank their is suspose to be some sort on insulator to prevent galvonic reactions from the dissimiliar metals with a ground wire bridging the connection. On the subject of PVC versus copper I would much rather have PVC for a number of reasons corrosion being number one on the list. Good luck sounds like you've got quite a project to keep you busy.
 
looks like electrolysis. If it in fact is there are measures that a proactive shop up on technology can guard against. It is a huge problem in coastal areas. It has eaten up the bridges on the west coast so bad that they are now experimenting with changing new construction to stainless rebar. If it is electrolysis there are ways to install galvanic protection but I don't have a clue how they do it.
 
Thanks for all of the answers! What a great group!

To answer some questions: Gas waterheater. Home owners does not cover. No anode on the external lines from the heater. Heater is 8 years old, original. There is no AC or DC voltage or current from the hot water pipe in the ground or at the water heater to house ground, to ground rod and to the cold water pipe measured with a sensitive DVM.

We will be replumbing with flexable plastic through the attic. The problem is that we have to trust the 1/2" cppper pipe to the sink, since it is in essence on an Island (access from the ceiling is almost impossiable.

The hole in the pipe was on the bottom. The exfoliation of the layers of pipe were external. The bore of the pipe is clean and no corrosion. There was no debris or particlulate matter in the water heater when drained.

Hole in the pipe:

copper_pipe_005.jpg
 
Two questions-
Was the copper wrapped?
Can you see the marking on what is left of the copper?

Copper buried in the ground should be wrapped, especially if you have corrosive soils in your area.

Copper used for water supply should be no less than Type L. You can identify Type L by the blue marking on the copper. If the copper has red (Type M) marking, you should have the builder replace at his cost-- it will not meet code.
Type M is allowed above ground in, or on, a building or underground outside of structures.

Good luck
 
The lot is on a sand peninsula. 6 feet of sand was removed, and 12 feet of "Red dirt" from Alabama was put on the lot, impacted and allowed to settle for 3 years before bulding the house. This dirt is high in iron content, I am not sure about other minerals, but it is not from salt water areas.

Here is a photo of the pipe end and the material which exfoliated from it in the "red dirt".
copper_pipe_003.jpg

The intact pipe is the cold water pipe and there is absolutely no evidence of corrosion.
 
Does not look like the copper was wrapped.

I would personally stay away from PEX piping (plastic)- if you do go with PEX, do not use within 18" of the water heater. Be sure they do a water pressure test on the new system, not less than the operating pressure from your water company (PEX can be air tested at 50psi) This test must be at least 15 minutes with no leaks or loss of pressure.

We had the same problem 3 or 4 years ago. The house was built in the mid '80s. We re-plumbed both hot and cold over head with the re-circulating pump. We also added isolation valves for each bathroom, the kitchen and the laundry room- in case we need to shut something off, we still have use of the other areas.

Good luck,

Roger
 
My BAD--- Looks like you would be under the I-Codes in Florida.
Type M copper is acceptable under the slab. :shock:

Here, in CA, we are still using the Uniform Plumbing Code.

Roger
 
As long as you will be re-plumbing, I'd second Roger's suggestion to put in isolation valves where possible and where it makes sense. I re-plumbed my old house with plastic pipes (to replace 40yr+ old galvanized hot water pipes) and put isolation valves in several locations. Makes it a lot easier to work on in the future.
 
Actually I keep turning down the water temp, and when I go out of town, somehow, the thermostat keeps going up!

I wish that the pipes were wrapped. Currently they are, but were not apparently in 2000. There were changes in the code in our county in 2001, but this house was finished (or at least started before the code was changed).

The water pressure was 60 PSI when we checked it the other day. The remaining copper pipes will be tested at 100 PSI (air). The Dura-Pex is rated at 100 PSI @ 180 F. The Pex is installed at least 10 feet from the water heater (pipe run distance, and will trace the path of the bad pipe, but going through the attic rather then under the slab.

The isolation valves sound like a good idea.

The water supply is city water. I don't know the pH, but can check it very easily.

As far as liability---that is a tough one. I doubt that anyone will own up to that, and any legal fees would exceed the costs of the repair. The builder has an excellent reputation. They are currently building both spec and developement houses, even in this environment, so seem to be a solid company. The home builder is aware of the problem, but I suspect that they will buck down the liability to the pipe manufactuer. I have no way of knowing what this pipe was. The plumber did talk to the plumber who did the rough in, but he does not remember the details. It is a custom home, so without mass production documentation. (if that even exists). After the job is completed I will approach the builder again --I gave them the option of having their plumber look at the work and they declined.
 