Wow. I've got a lot to learn about electricity.
I am establishing electric service to my property. I built the temporary service to building specs, including a meter base and a service panel - just got it inspected and approved. It is a 100 amp temporary service. The electric company will bring in the meter and wire to connect (direct burial) to the temp, but their wire will support a 200 amp service when connected to the house, whenever that may happen.
From the temporary pole, I installed a 220 50 amp breaker to supply the electric on the dock (a fuse panel) - consisting of a Tide Tamer 10,000 lb. lift with two 120 motors. It will also have a 30 amp plug for shore power to the boat and a 15 amp plug for incidentals. All of the dock "devices" are 110.
The dock builder and I ran 10-3 copper with a ground uf for this supply about 270 feet to the entrance of the "boardwalk" over the protected area, where I will install a disconnect. At his suggestion and experience, the wire was NOT put in conduit but attached under the dock with plastic clamps - not staples which corrode. His position is that in his 25 years experience, he has never seen a piece of conduit not leak. In our location, the few if any times water will reach the wire would be in a hurricane or like incident. I chose to defer to his experience.
From the disconnect to the 50 amp breaker in the temporary service is the run I am concerned with. I was told that #8 wire is needed to carry the 50 amps to the cut off. No problem, I can do that. But there is this great deal on #10@ 34 cents a foot, that if allowed to parallel, would not only save me some money but also increase the wire rating - 2 #10 in parallel would be better than one number 8 - if it is doable and legal.
You all have given me a platform to think about and ask the local supplier.
I did not know that only conductors 1/0 or larger may be connected in parallel. See NEC 310.4(a). I will check it out. If that is the case, I will not do what is not by code. I will also compare with running wire in conduit and burying in the ground.
My thought is to carry a true 50 amps to the cutoff at the dock. Then I would have enough power to run down the dock. I just need the right run of wire from the breaker to the cut off that will deliver the power.
I need to get this settled because in a few weeks, I am going down to the property (Bath NC) and establish a water service to the property and to the dock. I already have the dock piped with 3/4" Schedule 40 pvc. It is time to connect to the water meter, run the water line to the "house" - temporary panel, and then on to the dock. I was told to use 1" pipe to the house then drop to 3/4 for the about 400 foot run to the dock. They said to use 3/4" on that run to increase pressure. This may be the subject for another topic, "Calling All Plumbers".
When I rent the "ditch witch" for the water line, I want to dig the ditch for the electric at the same time. Maybe I will just bury the two lines together --psych --- I know its a no no.
Thank you all for such great insight and knowledge. I will keep in touch.
And "keep your cards and letters coming"
John