Intro:
Master Electrician/ Electrical Adminstrator, 30 years in trade.
Some random info for you, only having your description, and limited info, these are only estimates (guesstimates) on my, and should not be used for the actual installation.
1) You have a 240 v single phase service (2 hots, 1 neut, 1 ground)
2) Do not install 120v 15 amp or 20 amp devices at the end of a 30 amp circut as previously suggested. These devices are only rated for the current (amps) they are marked with. You may have a device start to fail due to overcurrent, but the circut is not protected below 30 amps.
3) Probably the best way to install this if you are going to do it is to set a breaker panel at the far end near your pier. Run 2 hots, 1 neut and 1 ground from this point (ground may or may not need to be run the total distance depending on the interpretation of what you are doing and local codes. Split power into individual circuts at that point based on need.
4) The portion from your service(100amp breaker) to the pier panel is a feeder as per NEC, may be called something different in your locale depending on local codes and interpretations. Voltage drop in this portion of the circut is limited to 3%, 5% total at end of branch circuts. Size the circut down at the main breaker to say 50 amps by using fuses or circut breaker. The run from the 50 amp fuse to pier panel now becomes a 50 amp feeder. You can adjust feeder size down to 30 amps (min allowed by NEC) or up to 100 amps depending on your final load. Your min size may be vary depending on local codes.
5) Using a 3% drop limitation, my calculator shows 750ft, @ 240 volts @ 50 amps, @ 3% = 3/0 copper XHHW, don't have aluminum figures, we don't use it on our jobs, may be able to find it. Be careful using aluminum around salt water, as the corrosion factor is brutal.
6) 750ft 3/0 xhhw x 3 (2 hots, 1 neut) = 2250 ft x $9693.86/ 1000 ft (9/06 distributor prices from American Cable Mansfield, Mass, not sure what retail would be at your local) = $21,811.19, wire price. (Note, we would pay a good bit more that conductor where we live). Price may be more if you have to run ground conductor full length. Also may be less if neutral can be de-rated, but a lot of locales don't allow us to do that anymore. This wire type needs to be run in conduit, a direct burial type will be more per foot. Add in the cost of a run of conduit, min size 2", probably larger due to run length ( I'd hate to think of pulling a 750 ft run w/2 bends thru 2")
7) Add in cost of nema 3 or 4 panel at pier end, any associated breakers and fuses or breaker needed to size feeder down.
8) If you don't know proper grounding and bonding practices, add in cost of hiring someone who does. IT IS CRITICAL ( note emphasis) to have this installation correctly grounded and bonded.
9) My suggestion would be to hire a contractor or engineer to design this for you or at least give you a ballpark on the feasibilty. You can cheap out, and do things however you want, but if someone gets injured or killed due to your installation, even if they are on your property unknown to you, whatever amount of liability insurance you have will not be enough. I live in a state where someone has probably the least chance of of ever being sued due to negligence, and I never take chances. I have been consulted on on injury/ death cases for the plaintiffs, and I can assure you being the defendant in one of those cases is a place you don't want to be.