I believe we have some talk of apples and some talk of oranges going on here at the same time....

Grounding is an issue in 2 completely different situations. One is protecting against a surge due almost always to lightning; and the other is providing an Equipment Grounding Conductor (EGC.....this is the "green wire") to protect humans from a ground fault in a circuit. We've mixed up these 2 protective practices in this conversation.

B95054 is correct when he says: "....we have to understand why to ground in the first place. It is there to protect you and your appliances from surges.". But I presume B95054 is talking about a surge created by lightning. Only lightning surges need to be directed to the earth (Note electricity does not "seek the earth", but rather it seeks to return to its source by whatever and all paths it can find with the most amps flowing in the paths with proportionally lesser resistance.) In the case of lightning, going to the earth is going to its source; but in the case of home wiring, the source is the transformer down the street; or while on shore power, the source is the transformer supplying the power on the dock; or in the case of a inverter or generator, it seeks to go back to the inverter or generator from whence it came. As journey on explains, the use of the green wire (EGC) is totally different than the surge (lightning) case. The EGC is there in case there is a short to the metal case of the drill, toaster, or whatever appliance you are using. Since the ground (green wire) is connected to the metal case (or other conducting surface you might touch), if a short like this happens, the circuit breaker (over current device) trips since the green wire provides a ultra low resistance path back to the source (instead of your body perhaps being part of some other higher resistance path back to the source).

My project and discussion is about providing a EGC. I have no lightning protection on my boat, and I don't feel that I need any here in the PNW.

_________________
Sandy McKean
Purchased Tosca in 2014
Re-powered to Yammi 200 in 2015
Back to top
View user's profile Send private message Send e-mail
B95054



Joined: 19 Nov 2020
Posts: 27
City/Region: Maple Ridge
State or Province: BC
PostPosted: Thu Feb 04, 2021 7:54 pm    Post subject: Reply with quote

Surges are created by many more issues than lightning strikes. Actually over 75% of surges are created within the home. When you are using a high draw appliance and it shuts off abruptly a surge occurs, Surge Protective devices help but the ground rod is the path that the excess energy will ultimately follow.
On a floating ground you are correct....a breaker or fuse trips stopping the flow of electricity through the circuit.

_________________
Discovered the C Dory and think it will be my next boat. Currently looking for a good 23 foot cruiser.
Back to top
View user's profile Send private message
thataway



Joined: 02 Nov 2003
Posts: 21473
City/Region: Pensacola
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 25 Cruiser
Vessel Name: thataway
Photos: Thataway
PostPosted: Thu Feb 04, 2021 9:31 pm    Post subject: Reply with quote

Several thoughts: If you get a lightning strike--the grounding on the inverter will most likely be one of the least of your problems on a C Dory.

Since 2014, updated code required marinas to install Ground Fault Protection (GFP). which would trip at 30mA or more. ABYC recommended boat manufacturers install a similar safety device at the entry point of the boat’s shore power, called an Equipment Leakage Circuit Interrupter (ELCI). Great for new boats--not so good for our older batons.

Since 2018 many marinas which re-wired, were forced to set the ground fault current at the pedestals to 5 to 6 mA. This became a problem for many vessels, since their grounding systems were based on the older standard of 30 mA. Also the main circuit ground fault was set at 30 mA vs the older standard of 1000mA. There has been a technical bulletin clarifying the rule for individual boat slips vs "floating housing". The design engineer can now use the old standards and design a system at that level or below.

Many of the Marinas along the ICW and in the Southern states where hurricanes have demolished docks, and new replacement pedestals were installed are ones at issue.

So the transient boater is still subject to possible tripping of the ground fault protection device at many upgraded marinas. Inverters are close to the top of the list of appliances which will trip the ground fault interrupter. Corrosion of fittings, older Galvanic Isolators or faulty Galvanic isolators, as well as defective power cords are also on the list of problematic items aboard.

_________________
Bob Austin
Thataway
Thataway (Ex Seaweed) 2007 25 C Dory May 2018 to Oct. 2021
Thisaway 2006 22' CDory November 2011 to May 2018
Caracal 18 140 Suzuki 2007 to present
Thataway TomCat 255 150 Suzukis June 2006 thru August 2011
C Pelican; 1992, 22 Cruiser, 2002 thru 2006
Frequent Sea; 2003 C D 25, 2007 thru 2009
KA6PKB
Home port: Pensacola FL
Back to top
View user's profile Send private message Send e-mail
smckean (Tosca)



Joined: 18 Jan 2014
Posts: 975
City/Region: Guemes Island (Anacortes)
State or Province: WA
C-Dory Year: 2005
C-Dory Model: 25 Cruiser
Vessel Name: Tosca
Photos: Tosca
PostPosted: Fri Feb 05, 2021 12:41 am    Post subject: Reply with quote

Quote:
When you are using a high draw appliance and it shuts off abruptly a surge occurs.......the ground rod is the path that the excess energy will ultimately follow.

This is just not so. Assuming AC systems, any and all current that flows into a house via the hot leads from the meter, leaves the house via those same leads back to the meter (with any unbalanced current between the 2 hots carried on the neutral). The current supplied to your meter comes from, and returns to, the transformer mounted on the pole or in the vault that supplies your house. The exceptions to that are induced voltage by things like lightning strikes near your house, or the path back to the meter somehow getting disrupted. OTOH, the ground rod may add some stability to a system for stray voltages and such (usually industrial or medical environments), but definitely very little energy will ever flow to the earth via the ground rod since any earth/ground-rod contact has very high resistance and I = E/R).

The old adage that electricity seeks ground is a widely held myth.....even sometimes by electricians. Here's an excellent video on this:

https://www.youtube.com/watch?v=qNZC782SzAQ

P.S. Note the term "excess energy" would be measured in something like watts (ExI). An appliance can't create energy; all and any energy in the circuits has to come from the meter. However E can be converted into I and visa versa via inductance (i.e., a transformer). Since motors have windings, they can produce voltage spikes and even energy spikes as the stored energy in the magnetic field of their coils suddenly collapses. And that energy (and its associated voltage and amperage) is not going to flow into the earth via the ground rod while there is a far lower resistance path back to the transformer available via the leads to the meter.
Back to top
View user's profile Send private message Send e-mail
B95054



Joined: 19 Nov 2020
Posts: 27
City/Region: Maple Ridge
State or Province: BC
PostPosted: Fri Feb 05, 2021 9:40 am    Post subject: Reply with quote

The current comes into the house on the hot lead and returns to the transformer via the neutral. In a voltage surge situation, let’s use a surge protector as an example...the excess energy gets collected in a storage device. In most cases this is a capacitor. The surge protector is tied to ground and will bleed off to the ground and not back to the transformer. I will stake my 30 plus years reputation as a consultant to electrical and electronics engineers on this. An electrical circuit requires balanced power to flow and any imbalance requires either equipment to rebalance (ie a surge protector) or it gets absorbed by your appliances. Over current in appliances can cause anything from failure to fire and/or safety risks. In the case of the floating ground the breaker serves to stop all flow of electricity when the imbalance occurs because you have nowhere else for it to bleed off to.
And btw - yes over 75% of surges are generated inside the home. Utilities have huge surge suppressors on the line that greatly reduce the effects of lightning strikes and also have the equivalent of breakers on the line to interrupt the circuit rather than allow the surge into your panel.That is not to say that lightning strikes cannot make it into the home (and they do) but in general they are greatly attenuated and not the number one cause of over current failures.
Take the example of a welder. It uses a high draw with sudden stops. Every time there is an abrupt stop there is a wave of current that needs to go somewhere. Hence the need for large surge suppressors in machine shops. On a smaller scale think of anything that pulls a high draw in your home. Turn it off abruptly and it will affect the waveform of all other running circuits. This is an over current situation generated in the home know as a surge. This is the number one failure of electronics.
I’ll tell you a little story...
A few years ago we had a situation at a Sobeys store where they were burning out their flouresecent ballasts at a rate of one to two per day. They were complaining that ballasts are built too cheaply and were laying the blame on the manufacturer. When I went on site you could see that there was a GM plant on their right and a machine shop on their left. All on the same grid. When I explained to them that they likely had a dirty power scenario they put up an argument that their power was clean and gave a very similar argument as above that all excess power would return to the utility. Not their fault, most people don’t have a clear grasp on electrical but somehow I had to convince them. So I suggested they install a surge suppressor with a hit counter and we will evaluate it after thirty days. If there were less than a couple of hits I would pick up the tab for it. If there were more than a few hits they pick up the tab. We did it and 30 days later it had registered 72 hits with no ballast failures. At that time I also noticed they have a wall of TV sets so I spoke with the electronics dept manager and asked if he had any tv failures. He explained that they are garbage and he loses on to two TVs a month. They just don’t manufacture them like they used to he said. So I offered him the same deal. He took it and when I went back to follow up after a year they still had not lost another tv since the installation of the surge protector.
So yes excess current is generated internally and does not return to the transformer. One way or another it needs to find its way to ground. If the ground is overloaded you need to find a way to slow down the amount of surge it needs to handle but one way or another it needs either a ground to bleed off to or an interruption in the circuit to stop all electricity from flowing.
Back to top
View user's profile Send private message
smckean (Tosca)



Joined: 18 Jan 2014
Posts: 975
City/Region: Guemes Island (Anacortes)
State or Province: WA
C-Dory Year: 2005
C-Dory Model: 25 Cruiser
Vessel Name: Tosca
Photos: Tosca
PostPosted: Fri Feb 05, 2021 3:58 pm    Post subject: Reply with quote

B95054 wrote:
The current comes into the house on the hot lead and returns to the transformer via the neutral.

I'm afraid this is not so either.

Electric power comes to a house on 3 wires: 2 hots, and a neutral. The voltage between the 2 hots is 240v; and between either hot and the neutral is 120v (there are other voltages possible depending on the transformer, but this is normal at least in residential settings). Each of the 2 hots go to one or the other of the 2 busbars in the panel. Branch circuits peel off from one busbar in the panel or the other along with a neutral making a 120v circuit. You are right in one respect, in the branch circuits, power flows into the circuit via the hot and flows back via the neutral, but this is not so for the service conductors that energize the panel (the 2 hots and 1 neutral from your meter). One of the objectives of wiring a building is to balance the load on the 2 sides of the panel. If the loads are perfectly balanced (let's say each side of the panel has a 50 amp "turned on" load), then no current will flow in the service neutral. OTOH, if one side of the panel is drawing 40 amps and the other 50 amps, then 10 amps will flow on the neutral back to the transformer. This is perhaps easier to see if we talk about the 240v circuits in a home (stoves, dryers, etc). These circuits have no neutral, but just the 2 hots. Every electron that flows down one of the hots flows back on the other hot. So all the power in a 240v circuit flows from/to the transformer via the 2 hots and the neutral isn't involved at all. If the loads on the 2 sides of the panel for 120v circuits are exactly equal, no current flows on the neutral back to the pole just like is so for a 240v circuit.

This will be my last post on this thread.

P.S. Describing AC circuits can be confusing since we tend to think/speak as if circuits were all DC; that is, we say current flows down one conductor and back on the other. This is not really the case. In actuality, current is oscillating back and forth 60 times per second on the 2 hots in a sinusoidal pattern. In the branch circuits the power is oscillating back and forth on its hot and on its neutral. The 2 hots coming from the transformer are in opposite phase (i.e., 180°), and therefore at the panel the 2 busbars are also in opposite phase. Therefore, the flow on the neutral bar from the branch circuits on one side of the panel cancels the flow on the neutral bar from the branch circuits on the other side of the panel. If the current on each set of these two sets of branch circuits is exactly the same, then no current flows on the neutral since the current is the same but 180° out of phase, so in that situation no current flows back to the transformer on the service neutral.
Back to top
View user's profile Send private message Send e-mail
B95054



Joined: 19 Nov 2020
Posts: 27
City/Region: Maple Ridge
State or Province: BC
PostPosted: Fri Feb 05, 2021 6:08 pm    Post subject: Reply with quote

Absolutely correct and shame on me for attempting to oversimplify the flow of current into the house. There is still the issue of surges and how they are handled through the ground. But I will leave that subject alone. Suffice to say that leaving the ground unconnected as somebody posted above is a bad idea ( maybe that is just what I should have said in the first place and not over complicated things). I’ll leave it alone now too.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    The C-Brats Forum Index -> General Chat All times are GMT - 5 Hours
Goto page Previous  1, 2
Page 2 of 2

 
     Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum



Page generation time: 0.0471s (PHP: 68% - SQL: 32%) - SQL queries: 20 - GZIP disabled - Debug on