PostPosted: Thu Dec 20, 2007 1:28 pm    Post subject: Reply with quote

captd wrote:
The job is probably all wrapped up by now. But Thataway is right. I had the Hunky Dory for seven years the 30 amp system was installed at the factory. The cord was so bulky and all adapters were so expensive. I, like Flapbreaker, always used the short reducer cord, and carried a small Number 12 extension cord. Even when using an electric heater. 30 amps were totally unnessesary with the 22 ft'er.

Mike does your laptop have a built in transformer on it's cord? What you are saying is dangerous is what happens in your house at every receptical. The smallest breaker in you house is probably 15 amp. 20 amp for appliances in the kitchen.
captd


30 amps are unnecessary. However, that is what the outlets supply.
A 50' 30 amp cord can be nicely rolled up and stored in a small gym
bag. It doesn't get tangled up in other stuff that way. A 30 amp 50' cord
costs, what, $70 or so?

A 12 gauge cord may not be dangerous. I'd have to look it up. Since no one
actually makes a 12 gauge 30 amp cord, at least one that is UL rated,
one would assume it is dangerous. You can't seriously argue no one
makes something that would save copper because, what, companies
don't like to make cheapest possible device?

Don't confuse the draw you are purposely putting on the line with the
draw that could occur if there is a fault. Two different concepts.
The draw that could occur if a fault occurs is 30 amps, plain and
simple.

My laptop power supply is UL certified. The low voltage output is not
dangerous if the power supply has protection built in. See my previous
posts. This is a perfectly valid way of reducing the size of the wire needed
to a device while still having a safe installation. You could easily build
a small box with a 30 amp 10 gauge connector to the outlet, a 15 amp
breaker and 14 gauge output cord. Properly made, such a device would
be safe. But, it would hard to build for $70 if you have to buy the
parts.

Perhaps one of us should write to Seaworthy and get them to do an
article on the subject? I can't believe their case files don't contain
instances of fires caused by invalid shore power adapters.

Mike
Back to top
View user's profile Send private message Send e-mail Visit poster's website
flapbreaker



Joined: 26 Jan 2005
Posts: 878
City/Region: Hillsboro
State or Province: OR
C-Dory Year: 2006
C-Dory Model: 22 Cruiser
Vessel Name: Playin' Hooky
Photos: Playin' Hooky
PostPosted: Thu Dec 20, 2007 10:43 pm    Post subject: Reply with quote

Just to be clear, I have no intention of trying to plug into 30 amp service using a plain ol' extension cord. I did buy a 25' 30 amp shore power cable. I only use the 30amp to extension cord adapter to plug the boat in at home to charge the batteries. I wasn't sure if I was clear on that in the beginning.
Back to top
View user's profile Send private message
Cutty Sark



Joined: 11 Dec 2004
Posts: 462
City/Region: Kenmore, Sammamish Slough
State or Province: WA
C-Dory Year: 1989
C-Dory Model: 16 Angler
Vessel Name: TBD
Photos: Cutty Sark
PostPosted: Fri Dec 21, 2007 10:29 am    Post subject: Reply with quote

I have a question, what is needed to duplicate the factory shorepower setup? Obviously Shore power cord, inlet, 30 amp breaker and a GFCI outlet, but what else? Galvanic Isolator? I have Nigel Calders book, But cant seem to figure out exactly what I need to setup my shore power.

Sark
Back to top
View user's profile Send private message Send e-mail
marvin4239



Joined: 06 Feb 2007
Posts: 1165
City/Region: Jacksonville Florida/Wilmington NC
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 22 Cruiser
Vessel Name: C-FLE II
Photos: C-FLE II
PostPosted: Fri Dec 21, 2007 11:07 am    Post subject: Reply with quote

Factory setup now comes with a Galvanic Isolator. You'll need a distribution panel also.
_________________
marvin
Back to top
View user's profile Send private message Send e-mail
Cutty Sark



Joined: 11 Dec 2004
Posts: 462
City/Region: Kenmore, Sammamish Slough
State or Province: WA
C-Dory Year: 1989
C-Dory Model: 16 Angler
Vessel Name: TBD
Photos: Cutty Sark
PostPosted: Fri Dec 21, 2007 11:29 am    Post subject: Reply with quote

The distribution panel usually has the breaker in it right?

Sark
Back to top
View user's profile Send private message Send e-mail
marvin4239



Joined: 06 Feb 2007
Posts: 1165
City/Region: Jacksonville Florida/Wilmington NC
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 22 Cruiser
Vessel Name: C-FLE II
Photos: C-FLE II
PostPosted: Fri Dec 21, 2007 11:47 am    Post subject: Reply with quote

Cutty Sark wrote:
The distribution panel usually has the breaker in it right?

Sark


Yes. I'm walking out on my dock to get part numbers that I will post for you.
Back to top
View user's profile Send private message Send e-mail
marvin4239



Joined: 06 Feb 2007
Posts: 1165
City/Region: Jacksonville Florida/Wilmington NC
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 22 Cruiser
Vessel Name: C-FLE II
Photos: C-FLE II
PostPosted: Fri Dec 21, 2007 12:35 pm    Post subject: Reply with quote

marvin4239 wrote:
Factory setup now comes with a Galvanic Isolator. You'll need a distribution panel also.


The power inlet is a Marinco 30 AMP model 304EL-B

The Galvanic Isolator is Guest Model 2433

There are actually two panels one is for the 30 DP main breaker which switches the neutral as well as the hot wire. This panel feeds the distribution panel which is a 3 circuit distribution panel with 1 5 amp breakers and 1 10 amp and 1 15 amp breaker. One breaker is for the GFI the other is for the on board Guest 20 amp battery charger. The panels are made by SEA DOG and have no model number on them that I could find without removing them. They are about 4'' by 6''. You can see a picture of them in my album in the modifications first picture.
Back to top
View user's profile Send private message Send e-mail
marvin4239



Joined: 06 Feb 2007
Posts: 1165
City/Region: Jacksonville Florida/Wilmington NC
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 22 Cruiser
Vessel Name: C-FLE II
Photos: C-FLE II
PostPosted: Fri Dec 21, 2007 12:49 pm    Post subject: Reply with quote

The Sea Dog panel numbers are 423132 for the distribution panel it also has a reverse polarity light. The distribution panel number is 423142 and has a 5 amp 10 amp and 15 amp breaker.

Last edited by marvin4239 on Fri Dec 21, 2007 6:10 pm; edited 1 time in total
Back to top
View user's profile Send private message Send e-mail
Cutty Sark



Joined: 11 Dec 2004
Posts: 462
City/Region: Kenmore, Sammamish Slough
State or Province: WA
C-Dory Year: 1989
C-Dory Model: 16 Angler
Vessel Name: TBD
Photos: Cutty Sark
PostPosted: Fri Dec 21, 2007 1:47 pm    Post subject: Reply with quote

Thanks for all the info, thats exactly what I was looking for. Got to love this place.

Sark
Back to top
View user's profile Send private message Send e-mail
mikeporterinmd



Joined: 15 Sep 2006
Posts: 645

State or Province: MD
C-Dory Year: 2002
C-Dory Model: 22 Cruiser
Vessel Name: Shelly IV
Photos: Shelly-IV
PostPosted: Fri Dec 21, 2007 3:53 pm    Post subject: Reply with quote

flapbreaker wrote:
Just to be clear, I have no intention of trying to plug into 30 amp service using a plain ol' extension cord. I did buy a 25' 30 amp shore power cable. I only use the 30amp to extension cord adapter to plug the boat in at home to charge the batteries. I wasn't sure if I was clear on that in the beginning.


Oh! Well, of course. That's perfectly fine since you either have a 15 or
20 amp breaker. I do that all the time.

Mike
Back to top
View user's profile Send private message Send e-mail Visit poster's website
mikeporterinmd



Joined: 15 Sep 2006
Posts: 645

State or Province: MD
C-Dory Year: 2002
C-Dory Model: 22 Cruiser
Vessel Name: Shelly IV
Photos: Shelly-IV
PostPosted: Fri Dec 21, 2007 4:05 pm    Post subject: Reply with quote

Blue Sea http://bluesea.com/ makes some nice panels. I peruse their
website and then look up the part numbers on northeastmarineelectronics.com
and order from them. Most of this stuff, including chargers, can be had
for a substantial discount if you order online. If you are doing a CD-22,
look at my photo album.

The inlet location I chose is somewhat non-traditional, but I really like it.
No tripping over the cord when boarding. I was hoping it would let me
use a 25' cord at home, too. But, as luck would have it, the outlet is
on the wrong side of the slip.

On a CD-22, the run from the inlet at the transom to the panel over
the tank is less than 10', and therefore within spec. However, I chose
to run the cable in PVC conduit for extra protection. If the run is
longer than 10', you need a breaker near the inlet. I wouldn't be against
installing one there in any case, but didn't see a good location.

Oh, there is a seller on ebay for Ancor brand cable. You'll find 10 gauge
cable to be quite expensive, so it makes sense to order online. You
shouldn't use home style NM-B since it is solid conductor; you should
use stranded on a boat.

The inlet is still clean and shiny after the first season, but we are not in
salt water.

I did not install a galvanic isolator. I probably should. Defender marine has
the best selection I've seen. It's a hard call because there is so little metal
in the water on a CD-22. Of course, you must bond DC negative to AC
ground, but if you have Nigel Caulder's book, that requirement has been
hammered into your head!

Mike
Back to top
View user's profile Send private message Send e-mail Visit poster's website
mikeporterinmd



Joined: 15 Sep 2006
Posts: 645

State or Province: MD
C-Dory Year: 2002
C-Dory Model: 22 Cruiser
Vessel Name: Shelly IV
Photos: Shelly-IV
PostPosted: Thu Dec 27, 2007 12:48 pm    Post subject: Reply with quote

marvin4239 wrote:
One thing to think about is what you are attempting to do is being done in every home in america. Your table lamp probably has a 18 gauge cord good for 5 amps and it's plugged into a plug with either....


We just picked up a little ceramic house with a light weight, UL rated
light. The plug contains a 5 amp fuse to protect the light weight wire.
So, you are partially correct. Or perhaps lots of homes in America have
unsafe wiring.

Mike
Back to top
View user's profile Send private message Send e-mail Visit poster's website
marvin4239



Joined: 06 Feb 2007
Posts: 1165
City/Region: Jacksonville Florida/Wilmington NC
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 22 Cruiser
Vessel Name: C-FLE II
Photos: C-FLE II
PostPosted: Thu Dec 27, 2007 1:05 pm    Post subject: Reply with quote

We just picked up a little ceramic house with a light weight, UL rated
light. The plug contains a 5 amp fuse to protect the light weight wire.
So, you are partially correct. Or perhaps lots of homes in America have
unsafe wiring.

Mike[/quote]

Actually Mike I think many of the houses in America do have unsafe wiring. If you want to know why I think this just go out to any large housing project while they are roughing in the wiring and take a look. Some areas of the country have more stringent building codes for instance Chicago area still requires houses be wired in conduit. In Florida where I live and have been a licensed electrician for 35 years the people doing electrical work don't even have to be licensed. Inspection departments in my area are a joke. We just had a 6 story parking garage collapse here and while it isn't official yet it appears it was due to pvc conduit in the slabs being installed incorrectly (all bundled together) which weakened the slab. I agree if something has a UL listing it should be safe but isn't always. Sorry to drift of topic.
Back to top
View user's profile Send private message Send e-mail
marco422



Joined: 25 Sep 2008
Posts: 103
City/Region: Salt Spring Island
State or Province: BC
C-Dory Year: 2007
C-Dory Model: 16 Cruiser
Vessel Name: Gaiasika
Photos: Gaiasika
PostPosted: Tue Dec 30, 2008 6:13 pm    Post subject: Reply with quote

[quote="mikeporterinmd"]
If the cord is plugged into a 30 amp outlet and something damages the
cord and causes a short, how are you going to prevent more than 15
amps from flowing?

Mike[/quote]

I believe a short would lead to a temporary current of over 15 amps (in fact over 30 amps since resistance is almost zero) until the 30 amp breaker on the dock tripped, which would take only a second or two. Too short a time to cause a cord fire I think. Also, only the cord between the plug and the short would heat up, not the section beyond the short.

Current capacity for a given wire gauge is calculated for continuous use with existing heat dissipation (insulated, conduit or free air). It doesn't take into account very short periods of overcurrent due to shorts.

While the installation technically does not meet codes, I believe it is reasonably safe.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    The C-Brats Forum Index -> Electrical and Wiring All times are GMT - 5 Hours
Goto page Previous  1, 2, 3
Page 3 of 3

 
     Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum



Page generation time: 0.1535s (PHP: 83% - SQL: 17%) - SQL queries: 32 - GZIP disabled - Debug on