PostPosted: Thu Nov 30, 2006 1:35 pm    Post subject: Power to a pier Reply with quote

I need to run underground power to my pier from up near the garage/apt. The run will be about 750' (Seven Hundered and Fifty Feet) and will come from a separate power meter that has a 100 Amp main breaker on it. I want to have 110/220 at the pier to run lights(110), shore power(110) and the boat lift electric motors (probably 220 but they're not installed yet). I probably need two 20 amp 110 circuits and a 30 amp 220 circuit in the box at the head of the pier.

I'll probably run three phase power down there, 110 either side of neutral plus a ground wire. What size/type of wire should I run, as I said, it'll be underground...

Thanks

Charlie

_________________
CHARLIE and PENNY CBRAT #100
Captain's Cat II 2005 22 Cruiser
Thataway (2006 TC255 - Sold Aug 2013)
Captain's Cat (2006 TC255 - Sold January 2012)
Captain's Kitten (1995 CD 16 Angler- Sold June 2010)
Captain's Choice (1994 CD 22 Cruiser- Sold Jun 2007)
Potomac River/Chesapeake Bay
K4KBA
Back to top
View user's profile Send private message Send e-mail
joeC



Joined: 08 Nov 2005
Posts: 39
City/Region: sweeny, Texas
State or Province: TX
C-Dory Year: 2005
C-Dory Model: 22 Cruiser
PostPosted: Thu Nov 30, 2006 1:42 pm    Post subject: Pier Power Reply with quote

About double Ought, Which is welding cable that run is near impossible.
JoeC
Back to top
View user's profile Send private message Send e-mail
drjohn71a



Joined: 15 Jul 2004
Posts: 1820
City/Region: Wichita
State or Province: KS
C-Dory Year: 2007
C-Dory Model: 255 Tomcat
Vessel Name: Tom-a-Hawk
Photos: Tom-a-Hawk
PostPosted: Thu Nov 30, 2006 1:46 pm    Post subject: Reply with quote

For the cost of the copper for a run like that, you could buy and run a huge generator! John
Back to top
View user's profile Send private message Visit poster's website Yahoo Messenger
Captains Cat



Joined: 03 Nov 2003
Posts: 7313
City/Region: Cod Creek>Potomac River>Chesapeake Bay
State or Province: VA
C-Dory Year: 2005
C-Dory Model: 22 Cruiser
Vessel Name: Captain's Choice II
Photos: Captain's Cat
PostPosted: Thu Nov 30, 2006 2:16 pm    Post subject: Re: Pier Power Reply with quote

joeC wrote:
About double Ought, Which is welding cable that run is near impossible.
JoeC


I wouldn't think it "impossible".... Many houses have a run like that from the transformer on the pole to the house, and that's 3 phase 220 I'm pretty sure....I've got 200 amps in the big house here in No VA and the run is about that long. I guess I could look in the breaker box at the main and see what size the wire is from the street. It's underground.

I was looking to see if someone had a calculation that would definitively size the wire... doesn't necessarily have to be copper either. How about aluminum?

Charlie
Back to top
View user's profile Send private message Send e-mail
drjohn71a



Joined: 15 Jul 2004
Posts: 1820
City/Region: Wichita
State or Province: KS
C-Dory Year: 2007
C-Dory Model: 255 Tomcat
Vessel Name: Tom-a-Hawk
Photos: Tom-a-Hawk
PostPosted: Thu Nov 30, 2006 2:35 pm    Post subject: Reply with quote

Charlie.... I have done a similar thing,but with not so long a run. I looked in the "CABO", local building codes book which dictates the wire size for various distances. I am pretty sure some electrical internet site could do similar for you. They have special gray, waterresistant underground wire bundles for that. I think that same wire covering, however, is subject to ultra violet damage from sun exposure, so the codes require a conduit from 18-24 inches under ground (based upon our freeze depth here) up to the outlet box. Just have the run checked for obstacles such as gas, elelctric, water lines, cable, etc, then rent a ditcher and go for it. But copper costs will kill you right now!

John
Back to top
View user's profile Send private message Visit poster's website Yahoo Messenger
Sea Wolf



Joined: 01 Nov 2003
Posts: 8650
City/Region: Redding
State or Province: CA
C-Dory Year: 1987
C-Dory Model: 22 Cruiser
Vessel Name: Sea Wolf
Photos: Sea Wolf
PostPosted: Thu Nov 30, 2006 2:45 pm    Post subject: Reply with quote

Charlie-

Here's a LINK to a calculator to figure out your wire sizing. (Look near the bottom of the page.)

The local codes will have to also be addressed, but separately.

I'm surprised you can get 3-phase power to your house. We can't do that in suburbia, but in farm and rural country........... (Would be great for welding, big motors, etc.)

Joe.

_________________
Sea Wolf, C-Brat #31
Lake Shasta, California

"Most of my money I spent on boats and women. The rest I squandered'. " -Annonymous
Back to top
View user's profile Send private message Send e-mail
Captains Cat



Joined: 03 Nov 2003
Posts: 7313
City/Region: Cod Creek>Potomac River>Chesapeake Bay
State or Province: VA
C-Dory Year: 2005
C-Dory Model: 22 Cruiser
Vessel Name: Captain's Choice II
Photos: Captain's Cat
PostPosted: Thu Nov 30, 2006 3:22 pm    Post subject: Reply with quote

On rethinking it, I don't get three phase power, I should know that. It's 220 three wire, 110 either side of neutral and then a ground... Embarassed

Thanks for the calculator, I'll try it.

Well, it says that with 2AWG copper, i'll have a 6% voltage drop at the end of a 750ft run with a 60AMP load. It won't get that high, I'm sure and i can live with that even if it does. Looks like that's the way to go. Now to go rob a copper mine somewhere.

Thanks a lot Joe, right on as usual... Thumbs Up Thumbs Up

Charlie


Last edited by Captains Cat on Thu Nov 30, 2006 3:27 pm; edited 1 time in total
Back to top
View user's profile Send private message Send e-mail
thataway



Joined: 02 Nov 2003
Posts: 20812
City/Region: Pensacola
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 25 Cruiser
Vessel Name: thataway
Photos: Thataway
PostPosted: Thu Nov 30, 2006 3:25 pm    Post subject: Reply with quote

Definately go Aluminum. There are some relitatively cheap--that is relitatively!== three conductors plus neutral at Home Depot,Lowes for long runs that are in the #2 to #2/0. If you want 3% voltage drop you will go with 2/0. For 7 1/2 % voltage drop #2. This is assuming only a 30 amp load. What I do is run 230 volts/two legs down--30 amps each and then split the two to give a total of 60 amps 110. I suspect that you have single phase, being residential--but if it is an industerial area you might have 3 phase.

I have always found that putting in a conduit gave much better longivity--especially near salt water--and bring the conduit up well above any potential storm surge. Also see my post about boat wiring--I put a second ground rod in at the box on the dock. Drive it in the bottom, and run copper wire to it for the neutral.

I don' know what you are hoisting--but we run 110 motors with no problems for the Tom Cat 255--lift rated at 11,000 lbs. I run the two motors at the same time on a 30 amp 110 volt circuit--I could determine the load and voltage drop--but this house is only about 250 feet (Previous was a little over 500 feet) from the box.

_________________
Bob Austin
Thataway
Thataway (Ex Seaweed) 2007 25 C Dory May 2018 to Oct. 2021
Thisaway 2006 22' CDory November 2011 to May 2018
Caracal 18 140 Suzuki 2007 to present
Thataway TomCat 255 150 Suzukis June 2006 thru August 2011
C Pelican; 1992, 22 Cruiser, 2002 thru 2006
Frequent Sea; 2003 C D 25, 2007 thru 2009
KA6PKB
Home port: Pensacola FL
Back to top
View user's profile Send private message Send e-mail
akbpilot



Joined: 20 Jan 2006
Posts: 16
City/Region: Fairbanks
State or Province: AK
PostPosted: Thu Nov 30, 2006 5:26 pm    Post subject: Reply with quote

Intro:
Master Electrician/ Electrical Adminstrator, 30 years in trade.

Some random info for you, only having your description, and limited info, these are only estimates (guesstimates) on my, and should not be used for the actual installation.

1) You have a 240 v single phase service (2 hots, 1 neut, 1 ground)

2) Do not install 120v 15 amp or 20 amp devices at the end of a 30 amp circut as previously suggested. These devices are only rated for the current (amps) they are marked with. You may have a device start to fail due to overcurrent, but the circut is not protected below 30 amps.

3) Probably the best way to install this if you are going to do it is to set a breaker panel at the far end near your pier. Run 2 hots, 1 neut and 1 ground from this point (ground may or may not need to be run the total distance depending on the interpretation of what you are doing and local codes. Split power into individual circuts at that point based on need.

4) The portion from your service(100amp breaker) to the pier panel is a feeder as per NEC, may be called something different in your locale depending on local codes and interpretations. Voltage drop in this portion of the circut is limited to 3%, 5% total at end of branch circuts. Size the circut down at the main breaker to say 50 amps by using fuses or circut breaker. The run from the 50 amp fuse to pier panel now becomes a 50 amp feeder. You can adjust feeder size down to 30 amps (min allowed by NEC) or up to 100 amps depending on your final load. Your min size may be vary depending on local codes.

5) Using a 3% drop limitation, my calculator shows 750ft, @ 240 volts @ 50 amps, @ 3% = 3/0 copper XHHW, don't have aluminum figures, we don't use it on our jobs, may be able to find it. Be careful using aluminum around salt water, as the corrosion factor is brutal.

6) 750ft 3/0 xhhw x 3 (2 hots, 1 neut) = 2250 ft x $9693.86/ 1000 ft (9/06 distributor prices from American Cable Mansfield, Mass, not sure what retail would be at your local) = $21,811.19, wire price. (Note, we would pay a good bit more that conductor where we live). Price may be more if you have to run ground conductor full length. Also may be less if neutral can be de-rated, but a lot of locales don't allow us to do that anymore. This wire type needs to be run in conduit, a direct burial type will be more per foot. Add in the cost of a run of conduit, min size 2", probably larger due to run length ( I'd hate to think of pulling a 750 ft run w/2 bends thru 2")

7) Add in cost of nema 3 or 4 panel at pier end, any associated breakers and fuses or breaker needed to size feeder down.

Cool If you don't know proper grounding and bonding practices, add in cost of hiring someone who does. IT IS CRITICAL ( note emphasis) to have this installation correctly grounded and bonded.

9) My suggestion would be to hire a contractor or engineer to design this for you or at least give you a ballpark on the feasibilty. You can cheap out, and do things however you want, but if someone gets injured or killed due to your installation, even if they are on your property unknown to you, whatever amount of liability insurance you have will not be enough. I live in a state where someone has probably the least chance of of ever being sued due to negligence, and I never take chances. I have been consulted on on injury/ death cases for the plaintiffs, and I can assure you being the defendant in one of those cases is a place you don't want to be.
Back to top
View user's profile Send private message
Sea Wolf



Joined: 01 Nov 2003
Posts: 8650
City/Region: Redding
State or Province: CA
C-Dory Year: 1987
C-Dory Model: 22 Cruiser
Vessel Name: Sea Wolf
Photos: Sea Wolf
PostPosted: Thu Nov 30, 2006 5:45 pm    Post subject: Reply with quote

akbpilot-

Wow! Looks like ~$25k done right! Good analysis!

Charlie-

How about a generator in a metal building on a concrete slab?

Joe
Back to top
View user's profile Send private message Send e-mail
akbpilot



Joined: 20 Jan 2006
Posts: 16
City/Region: Fairbanks
State or Province: AK
PostPosted: Thu Nov 30, 2006 6:11 pm    Post subject: Reply with quote

EDIT TO ABOVE POST

Price seemed high when I looked it up on the internet, not sure about the website I used, not my standard price sheet, but I was looking for something in your area. I called my supplier. He quoted me $3270.00/ 1000ft, so 2250 ft @ 3.27 = $7357.50 for conductor. We're a non-profit utility, so not sure of the pricing scheme, but you probably could find a competitive price in your area. Probably $10,000 or less, give or take for materials total.
Back to top
View user's profile Send private message
Captains Cat



Joined: 03 Nov 2003
Posts: 7313
City/Region: Cod Creek>Potomac River>Chesapeake Bay
State or Province: VA
C-Dory Year: 2005
C-Dory Model: 22 Cruiser
Vessel Name: Captain's Choice II
Photos: Captain's Cat
PostPosted: Thu Nov 30, 2006 6:51 pm    Post subject: Reply with quote

Wow... Shocked I called a local place (Richmond) for a quote, they haven't gotten back to me yet. Found some cable on a General Cable website. Great analysis akbpilot, thanks a lot!

Joe, the generator idea is looking better and better. I've got two 7500 watt generators on wheels, with 12500 surge capacity, looks like I may be using one of them! Had no idea the cable run would cost that much...

Still need the trench, have to run fresh water down there. Unfortunately, I don't have a water generator!

I'll let everyone know what I decide and get pix too when the time comes.

thanks again...

Charlie
Back to top
View user's profile Send private message Send e-mail
thataway



Joined: 02 Nov 2003
Posts: 20812
City/Region: Pensacola
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 25 Cruiser
Vessel Name: thataway
Photos: Thataway
PostPosted: Thu Nov 30, 2006 7:09 pm    Post subject: Reply with quote

Several other thoughts--down size the power requirements.
Have the utility company put another power pole down by the dock.
I suspect that all of the options above would require permitting.

One of my friends got some "cheap" aluminum cables, and did not put them in sealed conduit--the insullation was poor, the voltage drop was huge and the cables shorted out in a year--poor purchase!

I would normally recommend copper--but with the price it is almost out of sight when you get the large sizes--but I didn't realize it was as much as akbpilot noted!
Back to top
View user's profile Send private message Send e-mail
thataway



Joined: 02 Nov 2003
Posts: 20812
City/Region: Pensacola
State or Province: FL
C-Dory Year: 2007
C-Dory Model: 25 Cruiser
Vessel Name: thataway
Photos: Thataway
PostPosted: Thu Nov 30, 2006 7:12 pm    Post subject: Reply with quote

Several other thoughts--
1. down size the power requirements.
2. Have the utility company put another power pole down by the dock.
I suspect that all of the options above would require permitting.
3. Use solar power for the boat's charging system.
4. alternative (belt drive off a small engine, hydraulic pump etc to run the hoist.

One of my friends got some "cheap" aluminum cables used, and did not put them in sealed conduit--the insullation was poor, the voltage drop was huge and the cables shorted out in a year--poor purchase!

I would normally recommend copper--but with the price it is almost out of sight when you get the large sizes--but I didn't realize it was as much as akbpilot noted! No wonder the crooks are stealing the condensors out of the airconditioning roof units!
Back to top
View user's profile Send private message Send e-mail
akbpilot



Joined: 20 Jan 2006
Posts: 16
City/Region: Fairbanks
State or Province: AK
PostPosted: Thu Nov 30, 2006 7:34 pm    Post subject: Reply with quote

thataway wrote:
Several other thoughts--
1. down size the power requirements.
2. Have the utility company put another power pole down by the dock.
I suspect that all of the options above would require permitting.
3. Use solar power for the boat's charging system.
4. alternative (belt drive off a small engine, hydraulic pump etc to run the hoist.

One of my friends got some "cheap" aluminum cables used, and did not put them in sealed conduit--the insullation was poor, the voltage drop was huge and the cables shorted out in a year--poor purchase!

I would normally recommend copper--but with the price it is almost out of sight when you get the large sizes--but I didn't realize it was as much as akbpilot noted! No wonder the crooks are stealing the condensors out of the airconditioning roof units!


Yeah,the price of copper is out of sight. We lost 1000' of 500mcm cable to some wire thieves, along with some other smaller runs. If I remember correctly it weighs about 2#/ft. 2000# @ $1.85/# for scrap, someone made off with a bundle. Cost us about 12K to replace it.
My experiences with AL wire and salt enviroment have been less then satisfactory. Had a guy lose a leg of his service to his boatyard shop. When we pulled out the old cable, one leg was corroded in half, looked like white powder inside the cable jacket for about 6 inches. jacket looked fine, but there must have been a nick in the cable which allowed water inside. Being inside PVC conduit, there was no clear path to ground, at least not enough to trip the main breaker. He said he had noticed some of the lights dimming and his bathroom fan was running kind of slow. Not sure how long he had been having a problem, but it must have been going on for a while.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    The C-Brats Forum Index -> Electrical and Wiring All times are GMT - 5 Hours
Goto page 1, 2  Next
Page 1 of 2

 
     Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum



Page generation time: 0.0638s (PHP: 53% - SQL: 47%) - SQL queries: 33 - GZIP disabled - Debug on